Y
Y
Yarosh8412018-04-10 15:55:22
Electronics
Yarosh841, 2018-04-10 15:55:22

Choosing an uninterruptible power supply?

You need a UPS for equipment to keep it for 15 minutes or more.
The set of equipment is as follows, 2 chromatographs, each 900VA each (if I translated it correctly, then 550 watts each),
another 220W chromatograph, a laptop about 100 watts (maximum), a PC with an i5 monitor without a video card - about 300 watts. later we will add a liquid chromatograph and a PC for it (consumption is unknown, but I think no more than 1000 watts),
the total load is no more than 2700 watts.
I looked at the option Energy UPS Pro-5000 24V (it has two batteries of 12v 100 Ah in parallel.) But it confuses "Time to switch operating modes No more than 6 ms"
6ms to switch to the battery and back. Is this normal for the operation of the equipment or critical?

Answer the question

In order to leave comments, you need to log in

1 answer(s)
E
evgeniy_lm, 2018-04-11
@evgeniy_lm

"No more than 6 ms" does not bother me for a good pulsed power supply, it will be like a small hindrance, but the word "Energy" is very strong.
You need to take something from APC, but that prices start at $2000. I would take a UPS to each device separately, but you need "15 minutes or more," and this is no longer a UPS function, but an inverter. Take a 4-5kW inverter like this